Deleting a point from an MNB controller in StruxureWare Building Operation

Issue

Deleting a point from an MNB controller in StruxureWare Building Operation results in the following error

Environment

StruxureWare Building Operation: All versions up to and including 1.5.x
I/A Series Micronet BACnet Controller

Cause

StruxureWare Building Operation does not support the deletion of points in the Application Folder of a MNB device. 

Resolution

To delete a point, disconnect the MNB controller from the network. Once StruxureWare Building Operation server is unable to communicate with the MNB device, it will allow the deletion of the point in the Application folder.

Take note that even though the point has been deleted from the AS Application folder, the point still exist in the MNB controller.