Convert a Xenta 121-HP to a Xenta 121-FC

Issue

Is it possible to convert a Xenta 121-HP to a Xenta 121-FC?

Product Line

TAC Vista

Environment

Xenta 121

Cause

The hardware controller was purchased as a heat pump or fan coil unit, and the opposite is needed for the software application.

Resolution

As of August 2011, it is possible.

  1. Download the NXE file and XIF file for the desired application
  2. Download the files to the Xenta 121 using Lonmaker or NL220

This will be blocked in the future.