Controller fails to backup to flash with error: "Unable to backup objects to flash ..."

Issue

Controller fails to backup to flash. See error message "Unable to backup objects to flash ..."

Product Line

Andover Continuum

Environment

Continuum Controllers

Cause

A Program or Function in the Controller is corrupt and can't be compiled or is blank and does not have any Plain English code in it.

Resolution

  1. Go to the config page
  2. Clear database backup
  3. Fix up or delete the offending programs
  4. Re-attempt to save the database to flash