New in the Community? Get started here

Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 
Announcements
Discover the Exchange Community Top members of July 
Discover the latest features your community has to offer: register to the webinar here

Controller fails to backup to flash with error: "Unable to backup objects to flash ..."

Issue

Controller fails to backup to flash. See error message "Unable to backup objects to flash ..."

Product Line

Andover Continuum

Environment

Continuum Controllers

Cause

A Program or Function in the Controller is corrupt and can't be compiled or is blank and does not have any Plain English code in it.

Resolution

  1. Go to the config page
  2. Clear database backup
  3. Fix up or delete the offending programs
  4. Re-attempt to save the database to flash
Tags (2)
Labels (1)
No ratings