Continuum Explorer very slow when launched.

Issue

When Continuum Explorer is launched it takes a very long time to update. 

Environment

  • CyberStation
  • WebClient
  • Continuum Explorer

Cause

When Continuum Explorer is launched it must populate all objects that reside at the root.  When there is a very large number of Personnel objects or other object types in the root, Continuum Explorer will be slow or unresponsive until this population process is complete.

Resolution

  • Create a Folder under the Root of Continuum Explorer and move personnel objects to this folder.
  • Consider doing this to other objects that exist in large numbers.