Communicate with both TACNV (TANV) and SNVT in the same device

Issue

Is it possible to communicate with both TACNV (TANV) and SNVT in the same device?

Product Line

TAC Vista

Environment

  • TAC Xenta 300, TAC Xenta 401, TAC Xenta 280
  • Menta

Cause

Want to use SNVT communication for connections to Lonworks devices and TACNV (TANV) for connections to other programmable TAC Xenta controllers.

Resolution

There are no problems with this, however you need to verify that the total number of TACNV and SNVT does not exceed the limit for your type of device.