Changes made using the STR-350/351 LonMaker Plug-In revert back to previous settings

Issue

After using the STR-350/351 as an I/O module to a Xenta programmable controller and then using STR-350/351 LonMaker Plug-In the changes made in the Plug-in default back to previous settings

Environment

  • Vista
  • LonMaker, NL-220
  • STR-350 Plugin

Cause

If the STR was added to the Menta application then the controller will continually update the STR with the settings programmed. Any changes made with the STR LonMaker Plug-In will then be overwritten.

Resolution

In order to use the STR 350/351 LonMaker Plug-In, the STR must not be set up in classic mode by adding it in the Menta application of the controller communicating with it. If the STR-350 has already been added to a Menta application it must be configured using the Menta application. Otherwise, the STR-350 should be removed from the Menta application before attempting to configure the STR-350 as a Lon node using the Plug-in.