Can the number of decimal places displayed be changed?

Issue

How to define the number decimal places displayed for a point?

Environment

Building Operation Workstation

Cause

The default resolution for displaying points is 2, there is no setting to change this in individual points on the Workstation.

Resolution

The number of displayed decimal places is read from the Workstation PC Windows Regional Options, change or customize the Windows Options to set the "No of digits after decimal" value as required. This setting applies to all displayed values except for graphics where the number of digits displayed can be defined in the graphic editor.

The Workstation will need to be restarted for this setting to be changed.

The screenshot below shows a setting of 2 decimal places, Windows allows the value to be changed from 0 through 9: