Can a G3 / AX Jace do fox tunneling?

Issue

Customer has a Jace-7 installed with two NICs.  It's installed with 3.7.106.
NIC 1 (192.168.1.101) is communicating with 3 other jaces on-site with IP addresses of 192.168.1.102, 103, & 104.
NIC 2  (public address) is accessed remotely with Workbench.
Is there a way to access the stations (remotely) running on 192.168.1.102, 103 & 104 with fox tunneling?

Environment

Niagara G3 / AX

Cause

There is no Enterprise Server on site, just the four Jaces.

Resolution

Jaces cannot act as Proxy Servers so fox tunneling is not supported on anything except a server.