COV subscription links are being lost between MNB controllers

Issue

COV subscription links are being lost between MNB controllers

Product Line

TAC IA Series

Environment

MNB Controller

Cause

This is caused specifically by changing certain required link properties or by removing the objects that contain the link data.

Resolution

See TPA-RKFD-08-0001.00 "Avoid accidentally removing COV subscriptions (links) between MNB controllers" on The Exchange Download Center.