BAS2800+ - A BAS2800+ backup is not available for this site.

Issue

A site backup is not available.

Product Line

BAS2800+

Environment

  • BAS2800+
  • Backup
  • No Index
  • Uploading

Cause

The site is stand alone and the backup is not available.

Resolution

To recover the site data carry out the following;

  • Use the Pocket Terminal programme to review the outstation node configuration.
  • Setup the BAS2800+ terminal to match the configuration observed from the node.

Using the BAS2800+ System Diagnostics;

  • Select the outstation number and then from the options menu, select "Transfer Files"
  • Select to transfer PNTFLE.REC from the outstation, to C:\BAS\Data\osn??\PNTFLE.REC

Shutdown BAS2800+

Locate and run the "No Index" utility.

Run the utility to create the index

Restart BAS2800+ and confirm that the points are available and can be displayed.

Please note the "No Index" utility cannot name the index segments, this will need to be done by hand.