BACnet RULES implementation to disable features such as readPropertyMultiple, COVs etc How to disable RPM (readPropertyMultiple), COVs etc services in AS/ES BACnet interface.

Issue

There are some BACnet devices that advertise support for services such as RPM, COV etc  but malfunction when the service is used.  An example of such device is the Johnson Controls TEC2627VVT which advertises support for RPM but fails to upload its objects when SBO uses RPM to get the object list.

Product Line

EcoStruxure Building Operation

Environment

  • BACnet
  • Automation Server
  • Enterprise Server

Cause

Some BACnet devices with inconsistent protocol implementation are unable to process some BACnet services such as RPM, COV etc.

Resolution

In versions 1.8.1 and onwards allows the user to create a rule under the BACnet interface to configure SBO not to use the service, the rule is then applied to particular BACnet devices specified by 'Vendor Identifier' and 'Model Name' creating in effect a black list of such devices.

After applying the hot fix follow these steps to create the rule:

 

Using a text editor such as 'Notepad' create a text file and enter the device's vendor ID (5)  and model name (TEC2627VVT) followed by the rule (no-rpm, no-cov ) using the format seen in the screen shot below. (You can name the file anything you want),

Save the file to desired location on the PC.


rpm.png
 

Under the BACnet interface create a new 'Document' object in the 'Application' folder. NOTE: the object MUST be named 'service_blacklist' all low case.

Click 'Next' then import the text file created in step 1 and save the 'Document' object.

 

Reboot the server.

NoRPM_WarmStart_new.PNG

 

Once the device is on the black list, SBO will not send 'readPropertyMultiple' requests to the device, it will use only single 'readProperty'.

 

When disabling RPM and COV for a particular device the blacklist would be as follows.

(no-COV rule added in 1.8.1.23701 and included in the later full release builds)

X
Y
         ---- if model claims rpm, but fails
         ---- if model claims cov, but fails
 
   
 rpm and cov.png
 
And this syntax can also be extended for multiple devices from different vendors at the same time.
 
multiple.png