Average space temperature on TAC Xenta 120 devices

Issue

Average space temperature on TAC Xenta 120 devices.

Product Line

EcoStruxure Building Operation, TAC Vista

Environment

  • TAC Xenta 121-FC
  • TAC Xenta 121-HP

Cause

TAC Xenta 121 is able to average space temperatures from multiple sensors. For example, it could average two room units, or one room unit and one Lon sensor.

It is possible to average up to three different Lon sensors.

Resolution

Bind a valid temperature SNVT value to the input nviSpaceTemp. The TAC Xenta 120 device will calculate the average between the bound input and the physical sensor.