Availability of TAC228R

Issue

Is the TAC228R controller still available?

Environment

  • TAC228R
  • 2281084000

Cause

Availability of old controller

Resolution

The TAC228R was withdrawn in 2011 and is no longer available for ordering for new projects. It will still be available as a spare part until 2021-12-31 when it will be terminated.

A suitable alternative is the SE8300 series of room controllers.

The TAC228R had the ability of a remote setpoint using a 0-10V signal, by using lua script and utilizing the input UI23, the same operation can be achieved.