Automation Server CPU usage between 80-100%

Issue

Automation Server CPU usage goes between 80-100% even with few programs, trends or alarms.

Product Line

EcoStruxure Building Operation

Environment

AS Automation Server

Cause

Cause 1: BACnet into AS uses a lot of resources

Cause 2: The AS has bindings from a point to a variety of places

Also check out the AS CPU and Memory Loading Quick-Help video on the Exchange.

Resolution

Example Resolutions in order:

  1. The issue described is Functions as Design in StruxureWare Building Operation. The AS results with high CPU percentage with just one point from BACnet interface loaded; however, it had no effect on AS performance.
  2. Check the propagation of values. An example would be a Space Temperature which is required by the field bus, the BACnet interface, LON interface, etc. Make sure to properly disseminate this value so to avoid overloading the CPU.