Alarm block limitation in a single Menta application

Issue

Generating a Menta application results in the following error if the maximum number of Menta blocks is exceeded in the application:

TAM32
The maximum number of Alarm blocks is exceeded in the application.
The problem must be solved before the application can be generated.

Environment

  • Menta
  • Xenta programmable controllers
  • Xenta 281, 282, 283, 301, 302, 401, 401:B

Cause

Generating a Menta application results in an error if the maximum number of Menta blocks is exceeded in the application.

Resolution

There can be no more than 127 alarm blocks in a Menta application.