Add Xenta trend log is grayed out when right clicking on point in a programmable Xenta controller and selecting Create Trend Log.

Issue

Add Xenta trend log is grayed out when right clicking on point in a programmable Xenta controller and selecting Create Trend Log.

Environment

  • Xenta Programmable Controller
  • Menta

Cause

There are no available trend logs in the Menta application. There have to be empty trend logs in Menta for this to work.

Resolution

  1. Edit the file In Menta
  2. Go to Options > Trend Logs
  3. Click on the 'up arrow' to increase the number of available trend logs.
  4. Save the application to the Vista Database
  5. Download to the controller.