Learn about the Community. Join our Core Community to Get Started

Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

Access Control power supplies and enclosures

Issue

Access Control power supplies in UK are not available globally.

Environment

Continuum ACX57 CX9702 PSU Power supply

Continuum enclosures

Cause

Power supplies for access control systems (for powering of door locks/maglocks etc) should be purchased locally.

Resolution

All of the globally available enclosures are detailed in the Enclosure Family Datasheet. This includes ones suitable for Netcontrollers, ACX's, bCX's, i2 and VAV controllers.

Power supplies for access control systems (for powering of door locks/maglocks etc) should be purchased locally to suit the site applications.


Product Support Services does not keep records of the equipment that may have been purchased locally.
e.g. in the UK a company called Dantech is used for Enclosures and power supplies, please contact them directly if PSU connection details are required.

Dantech electronic engineering
3 Galliford Road Industrial Estate
Heybridge
Maldon
Essex
CM9 4XD
Tel: +44(0)1621856850
NOTE: The Dantech PSUs often include FR contacts (Fire Relay) that need to be powered by 12Vdc to enable the supply.
 

Tags (1)
Labels (1)
No ratings