7798C cannot be used with I/NET 2000

Issue

Can I use the new 7798C in an I/NET 2000 System?

Environment

  • I/NET 2000
  • I/NET Seven rev 1.16 and above
  • 7798C SLI

Cause

AMT is different in I/NET 2000 than it is in I/NET Seven and any message and transaction from this SLI will not report correctly.

Resolution

You cannot use this SLI in I/NET 2000. Even if you load the 7798C Bin files into I/NET 2000 the SLI will not work.

This SLI is designed to ONLY operate correctly in I/NET Seven Rev 1.16 and above.