Posted: 2020-09-15 09:38 PM
Hi all,
I am setting up user configurable temperature and pressure unit support on a TM172DCLWTHP via EcoStruxure Machine Expert - HVAC.
I'm looking at changing the 'Temp_UM' parameter to change the on-board temperature reading and the sensor reading is directly tied to an edit box on the HMI. I have tried to write to it using the parameter link 'sysPar_Temp_UM' and the parameter name directly (Temp_UM) but I am receive no change in sensor values. I can change Temp_UM via Commissioning and it works just fine in changing unit type and the displayed value, and I can successfully read from sysPar_Temp_UM' in Programming.
During compile, I receive errors such as the following (when using sysPar_Temp_UM in Programming);
PROGRAM_MAIN(41) - error G0008: ST => Invalid access to variable
Or when I attempt using 'Temp_UM' in Programming;
PROGRAM_MAIN(39) - error A4097: TEMP_UM => Object not found
How do I go about fixing this so that I have access to 'Temp_UM'?
Cheers,
Jack
Posted: 2020-09-16 12:51 AM
Dear @obscuresc ,
I have used the following code in the programming tab of the TM172D:
IF xPET_Select_C THEN
xAux := sysWriteParUINT(ADR(sysPar_Temp_UM), 0); //C
xPET_Select_C := FALSE;
xPET_Select_F := FALSE;
END_IF;
IF xPET_Select_F THEN
xAux := sysWriteParUINT(ADR(sysPar_Temp_UM), 1); //F
xPET_Select_C := FALSE;
xPET_Select_F := FALSE;
END_IF;
You can check the behaviour in the next video:
https://schneider-electric.box.com/s/5emuv4ach0vwj0e9kx28qg2zqc6r2jm1
https://schneider-electric.box.com/s/5emuv4ach0vwj0e9kx28qg2zqc6r2jm1
Let us know if this works for you.
Best regards,
Leandro
Posted: 2020-09-16 12:51 AM
Dear @obscuresc ,
I have used the following code in the programming tab of the TM172D:
IF xPET_Select_C THEN
xAux := sysWriteParUINT(ADR(sysPar_Temp_UM), 0); //C
xPET_Select_C := FALSE;
xPET_Select_F := FALSE;
END_IF;
IF xPET_Select_F THEN
xAux := sysWriteParUINT(ADR(sysPar_Temp_UM), 1); //F
xPET_Select_C := FALSE;
xPET_Select_F := FALSE;
END_IF;
You can check the behaviour in the next video:
https://schneider-electric.box.com/s/5emuv4ach0vwj0e9kx28qg2zqc6r2jm1
https://schneider-electric.box.com/s/5emuv4ach0vwj0e9kx28qg2zqc6r2jm1
Let us know if this works for you.
Best regards,
Leandro