Temp_UM parameter is inaccessible from Programming and Display on TM172

Solved
obscuresc
Ensign
Ensign
0 Likes
2
980

Temp_UM parameter is inaccessible from Programming and Display on TM172

Hi all,

 

I am setting up user configurable temperature and pressure unit support on a TM172DCLWTHP via EcoStruxure Machine Expert - HVAC.

 

I'm looking at changing the 'Temp_UM' parameter to change the on-board temperature reading and the sensor reading is directly tied to an edit box on the HMI. I have tried to write to it using the parameter link 'sysPar_Temp_UM' and the parameter name directly (Temp_UM) but I am receive no change in sensor values. I can change Temp_UM via Commissioning and it works just fine in changing unit type and the displayed value, and I can successfully read from sysPar_Temp_UM' in Programming.

 

During compile, I receive errors such as the following (when using sysPar_Temp_UM in Programming);

 

PROGRAM_MAIN(41) - error G0008: ST => Invalid access to variable

 

Or when I attempt using 'Temp_UM' in Programming;

 

PROGRAM_MAIN(39) - error A4097: TEMP_UM => Object not found

 

How do I go about fixing this so that I have access to 'Temp_UM'?

 

 

Cheers,

Jack

 

 

Tags (1)

Accepted Solutions
LeTomas
Lieutenant Lieutenant
Lieutenant
0 Likes
1
967

Re: Temp_UM parameter is inaccessible from Programming and Display on TM172

Dear @obscuresc ,

 

I have used the following code in the programming tab of the TM172D:

 

IF xPET_Select_C THEN

xAux := sysWriteParUINT(ADR(sysPar_Temp_UM), 0); //C
xPET_Select_C := FALSE;
xPET_Select_F := FALSE;
END_IF;

 

IF xPET_Select_F THEN

xAux := sysWriteParUINT(ADR(sysPar_Temp_UM), 1); //F
xPET_Select_C := FALSE;
xPET_Select_F := FALSE;
END_IF;

 

You can check the behaviour in the next video:

https://schneider-electric.box.com/s/5emuv4ach0vwj0e9kx28qg2zqc6r2jm1

https://schneider-electric.box.com/s/5emuv4ach0vwj0e9kx28qg2zqc6r2jm1 

 

Let us know if this works for you.

 

Best regards,

 

Leandro

See Answer In Context

Tags (1)
2 Replies 2
LeTomas
Lieutenant Lieutenant
Lieutenant
0 Likes
1
968

Re: Temp_UM parameter is inaccessible from Programming and Display on TM172

Dear @obscuresc ,

 

I have used the following code in the programming tab of the TM172D:

 

IF xPET_Select_C THEN

xAux := sysWriteParUINT(ADR(sysPar_Temp_UM), 0); //C
xPET_Select_C := FALSE;
xPET_Select_F := FALSE;
END_IF;

 

IF xPET_Select_F THEN

xAux := sysWriteParUINT(ADR(sysPar_Temp_UM), 1); //F
xPET_Select_C := FALSE;
xPET_Select_F := FALSE;
END_IF;

 

You can check the behaviour in the next video:

https://schneider-electric.box.com/s/5emuv4ach0vwj0e9kx28qg2zqc6r2jm1

https://schneider-electric.box.com/s/5emuv4ach0vwj0e9kx28qg2zqc6r2jm1 

 

Let us know if this works for you.

 

Best regards,

 

Leandro

Tags (1)
obscuresc
Ensign
Ensign
0 Likes
0
950

Re: Temp_UM parameter is inaccessible from Programming and Display on TM172

Hi @LeTomas,

 

Thanks for you help, I had forgotten these functions existed.

I ported your solution to the Display tab and it worked as expected.

 

Cheers,

Jack