I enabled the webserver on my ST6500 HMI. When I tried to connect to the panel there was no web-page available (http error 404).
Is there a manual/example available for the webserver? The help-file in EOTE is , as always, very scarce with information.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-09-29 08:51 AM . Last Modified: 2020-09-30 08:25 PM
Hello,
The ST6500 today only supports the Web API functionality. This means writing your own code to use HTTP requests or websockets to access read only variables/alarms. Still a web server but not for generic web page access.
When we offer version 3.2, which is expected in early 2021, you will be able to connect using a regular web browser and view the HMI screens using the Web GUI (Graphic User Interface) in synchronous mode. Full read/write access should be available.
Keep an eye out for version 3.2 :).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-09-29 08:51 AM . Last Modified: 2020-09-30 08:25 PM
Hello,
The ST6500 today only supports the Web API functionality. This means writing your own code to use HTTP requests or websockets to access read only variables/alarms. Still a web server but not for generic web page access.
When we offer version 3.2, which is expected in early 2021, you will be able to connect using a regular web browser and view the HMI screens using the Web GUI (Graphic User Interface) in synchronous mode. Full read/write access should be available.
Keep an eye out for version 3.2 :).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-15 04:15 AM
Dear Paul,
We would like to use Web GUI feature in the ST6400.
However, Do we have to use or order an API code to activate Web GUI?
If so, could you inform us about code and licence informations for WEBGUI?
Is it possible to use it as free or trial at the moment?
Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-17 12:46 AM
Hey,
I asked the same question to a schneider rep. recently and got this in response:
HMIWRT001 1 EOTE webviewer keycode - 1 pc 50,00 euros brut
HMIWRT010 1 EOTE webviewer keycode - 10 pcs 200,00 euros brut
HMIWRT100 1 EOTE webviewer keycode - 100 pcs 600,00 brut
discount code: TAK
Don't know if the prices are the same in your region but maybe this helps.