  • SCADAPACK 535E configuration lost
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49250members
Join Now
242460posts
Join Now

SCADAPACK 535E configuration lost

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to Industry Automation and Control Forum
Solved
OsamaSalih
Ensign OsamaSalih
Ensign
‎2020-02-23 05:53 AM
0 Likes
11
1596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-23 05:53 AM

SCADAPACK 535E configuration lost

Hi everyone

 

The plant where I work has multiple SCADAPACK 535E RTUs utilized in a remote location for monitoring and control the process.

The whole configuration is randomly lost (both SCADAPACK E configurator and ISAGRAF SCADAworkbench) applications are lost , the RTUs return to factory default

 

When that happens, I need to switch off the power for a period of time (one day minimum) and come again later to download the files because the device does not accept the files without doing that, although the programs indicate that the files has been downloaded successfully, but actually nothing changed in the device, and I have to keep the device turned off for a day or two before I can repeat the task with success.

 

Please advice

Osama

BAPCO pipeline

 

 

 

 

Solved! Go to Solution.

Labels
  • Smart Design & Engineering
Share
Reply

Accepted Solutions
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-02-28 05:02 PM
0 Likes
1
1508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-28 05:02 PM

Re: SCADAPACK 535E configuration lost

If you have a SP535E (i.e. not a SP530E) then it has a 6601 IO module inside it.

There is the controller board on top, and then the IO board at the bottom.

It's why the SP535E has the exact same footprint as the 6601 IO module.

 

The address of this inbuilt module is 0, and it can't be changed, which is why there is a metal cover over the part where you would normally access the DIP switch to change the IO module address.

 

There are separate 'firmwares' here:

  1. Controller Firmware
  2. Controller Boot Monitor
  3. IO Firmware
  4. IO Bootloader

 

The SP535E has all four of these on-board, the first two on the controller, the second two on the IO module.

If upgrading all, then you have procedures to follow to upgrade all individually (taking care to perform them in the correct order).  It's all spelled out in the Release Notes, and the User Manual.  Even the Hardware Manual has a reference to this information.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
11 Replies 11
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-02-23 06:03 AM
2 Likes
5
1593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-23 06:03 AM

Re: SCADAPACK 535E configuration lost

What firmware versions are these 535E RTUs running?

There was a known issue with a certain firmware (I think it was 8.14.1 or such) that would result in the configuration of the RTU going corrupt after a certain period of time.  When this happened it would indeed lose both the configuration, and the ISaGRAF code.

 

It seems it's a little difficult to find links to the software to download

https://www.se.com/us/en/product-range-download/61250-scadapack-e/?parent-category-id=88847&parent-s...

 

Based on this, it seems that 8.14.7 might be the most appropriate version to be running.

 


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-02-23 06:07 AM
1 Like
1
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-23 06:07 AM

Re: SCADAPACK 535E configuration lost

PS: You will find that if you Factory Reset the device (following the guidance in the user manual) that you will be able to download to the device immediately.

The reason that leaving it turned off for a day or two is working is that it is likely causing the small Lithium battery internal to the unit to become exhausted, at which point the configuration is no longer 'corrupt' but wiped.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
OsamaSalih
Ensign OsamaSalih
Ensign
‎2020-02-25 10:19 AM
0 Likes
0
1572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-25 10:19 AM

Re: SCADAPACK 535E configuration lost

Hi @BevanWeiss

Thank you for your valuable responses😀

 

the firmware of the rPACs is 8.14.3

 

I check for the release notes and yes there are some firmwares that had  bugs

 

now I downloaded the software and preparing to install it soon in the 3 rPACs

 

I have found version 8.15.1

which was released in 2020😀

I am going to update firmware+bootloadet for the rPAC and the same will be done to the 6601 extensions modules which two out of three of rPACs have it  installed

IMG-20200225-WA0115.jpg

 

Share
Reply
OsamaSalih
Ensign OsamaSalih
Ensign
‎2020-02-25 10:32 AM
0 Likes
0
1571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-25 10:32 AM

Re: SCADAPACK 535E configuration lost

I actually following the procedure as instructed in the manual, but getting same results, I always have to switch off for a day or two, I hope this will not be the case when installing the firmware 😔

Share
Reply
OsamaSalih
Ensign OsamaSalih
Ensign
‎2020-02-25 11:42 PM
0 Likes
3
1565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-25 11:42 PM

Re: SCADAPACK 535E configuration lost

I have some questions before I proceed to firmware upgrade 

 

1/ what is the correct order for performing the upgrade for :

* RTU firmware upgrade

* RTU boot monitor upgrade

* 6601 module firmware upgrade

* 6601 module boot monitor upgrade

 

is this order correct?

 

2/ Is the boot monitor is the same as boot loader, if not what is the difference?

 

 

3/ I am going to make all the firmware upgrades online through USB cable

Will that keep the configuration files (E-configuarator and Workbanch) so no need to download these again?? 

Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-02-25 11:59 PM
0 Likes
2
1560
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-25 11:59 PM

Re: SCADAPACK 535E configuration lost

1) What does the manual say?

 

2) Yes, the boot monitor, and boot loader are the same.

 

3) I'd recommend using the Ethernet connection and FTP to transfer the firmware files across, then do a patch restart (as detailed in the manual).  It's significantly faster.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
OsamaSalih
Ensign OsamaSalih
Ensign
‎2020-02-27 04:57 AM
0 Likes
1
1556
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-27 04:57 AM

Re: SCADAPACK 535E configuration lost

I have finshed one out of three firmware update for my 535e rPACs

 

the order of update is in same order as in my last reply 

 

Now new question rise up

1/ in the Scadapack 535E hardware manual, it is mentioned that if you started E-configurator for a specific RTU, it is not possible swigch to clearscada software,(see attached pic) 

 

Does that mean I have to stop my ClearScada RUNTIME before I can download the configuration file to the RTU of which Clearscada polls process data from ?

 

2/ In the firmware version 8.14.7 release webpage 

 

https://tprojects.schneider-electric.com/telemetry/display/public/General/SCADAPack+E+Utilities+Disc...

 

it is saying " The command line command “restart iofirm <filename> <module address>” is provided for 6601 firmware upgrades (see attached photo) 

 

My question is how to determine the module adress ??? 

 

IMG-20200227-WA0082.jpg

Screenshot_20200227_145133_com.android.chrome.jpg

 

Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-02-27 05:14 AM
0 Likes
0
1552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-27 05:14 AM

Re: SCADAPACK 535E configuration lost

1) That document is a liar.  I think it's just bad wording, I'm pretty sure it's trying to say that if you change the RTU configuration using E-configurator, that you can't expect this change to be reflected within ClearSCADA.  If you later change the config in ClearSCADA it will overwrite anything you had changed within E-Configurator.  Similarly the other way around.  Although with E-Configurator you can always Read the config from the RTU, which should match what it really is (as long as you've restarted the RTU since changes..)

So no, don't shutdown ClearSCADA or anything.

 

2) Yes, if you're talking about additional IO modules then you should enter the module address of the module you want to upgrade.  You should know what this number is, it's either shown when you read the IO Modules list from E-configurator, or it's the number the DIP switch is pointing to on the expansion IO.  You don't have to upgrade the base IO, this is done automatically.  I believe that the first IO module attached is also done automatically, the firmware upgrade process listing in the manual has all of these details I'm sure.

 

PS: That link you sent is NOT the manual.  The manual would be found from within E-Configurator in the Help section.  It's a much better source of information about upgrading firmware.  ONLY when the release notes tell you do deviate from the manual should you do so.  DO NOT assume the release notes provide all the information that you need.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
OsamaSalih
Ensign OsamaSalih
Ensign
‎2020-02-27 06:21 AM
0 Likes
2
1543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-27 06:21 AM

Re: SCADAPACK 535E configuration lost

Thank you @BevanWeiss

 

NOW FOR THE RTU THAT I ALREADY UPDATED, IT IS SHOWING 6601 I/O ver 1.77. 43 , WHICH IS SAME VERSION ALREADY EXISTED 

ALTHOUGH THIS RTU  IS NOT CONNECTED TO ANY 6601 EXTENSION MODULE

 

DOES THE 6601 FIRMWARE AND BOOT MONITOR SAVED TO THE RTU MEMORY OR TO THE MODULE ITSELF??

 

AND SHOULD I UPDATE THAT TOO? 

IMG-20200227-WA0123.jpg

 

Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-02-28 05:02 PM
0 Likes
1
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-28 05:02 PM

Re: SCADAPACK 535E configuration lost

If you have a SP535E (i.e. not a SP530E) then it has a 6601 IO module inside it.

There is the controller board on top, and then the IO board at the bottom.

It's why the SP535E has the exact same footprint as the 6601 IO module.

 

The address of this inbuilt module is 0, and it can't be changed, which is why there is a metal cover over the part where you would normally access the DIP switch to change the IO module address.

 

There are separate 'firmwares' here:

  1. Controller Firmware
  2. Controller Boot Monitor
  3. IO Firmware
  4. IO Bootloader

 

The SP535E has all four of these on-board, the first two on the controller, the second two on the IO module.

If upgrading all, then you have procedures to follow to upgrade all individually (taking care to perform them in the correct order).  It's all spelled out in the Release Notes, and the User Manual.  Even the Hardware Manual has a reference to this information.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Share
Reply
OsamaSalih
Ensign OsamaSalih
Ensign
‎2020-02-29 08:55 AM
0 Likes
0
1499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-02-29 08:55 AM

Re: SCADAPACK 535E configuration lost

Thank you @BevanWeiss

That makes sense 

 

I will perform all upgrades possible

Share
Reply
Top Experts
User Count
andrea_romacco
Crewman andrea_romacco
1
Fleo
Crewman Fleo
1
sesa25402
Administrator sesa25402 Administrator
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric