Posted: 2020-05-20 10:48 AM
If you want OPC UA Server expert to trust your client, you have to add the client's certificate in the trusted certificate list.
Run this tool - "C:\Program Files (x86)\Schneider Electric\OPC UA Server Expert\PKI\OPCUA ServerExpert.msc" - and import your client's certificate in the OFSUA_CTL\Certificates folder.
Posted: 2020-05-20 02:47 AM
Hello @kingslim .
Could you help with this?
Regards,
Rodrigo G.
Industrial Automation Community manager
Posted: 2020-05-20 10:48 AM
If you want OPC UA Server expert to trust your client, you have to add the client's certificate in the trusted certificate list.
Run this tool - "C:\Program Files (x86)\Schneider Electric\OPC UA Server Expert\PKI\OPCUA ServerExpert.msc" - and import your client's certificate in the OFSUA_CTL\Certificates folder.