Hi Everyone,
I'm trying to add my application to Trust in OFS OPC UA. I'm getting an error" Does not have a Trust list defined". How to solve it?.
Regards,
Praveen raj.k
Solved! Go to Solution.
If you want OPC UA Server expert to trust your client, you have to add the client's certificate in the trusted certificate list.
Run this tool - "C:\Program Files (x86)\Schneider Electric\OPC UA Server Expert\PKI\OPCUA ServerExpert.msc" - and import your client's certificate in the OFSUA_CTL\Certificates folder.
Hello @kingslim .
Could you help with this?
Regards,
Rodrigo G.
Industrial Automation Community manager
If you want OPC UA Server expert to trust your client, you have to add the client's certificate in the trusted certificate list.
Run this tool - "C:\Program Files (x86)\Schneider Electric\OPC UA Server Expert\PKI\OPCUA ServerExpert.msc" - and import your client's certificate in the OFSUA_CTL\Certificates folder.