Modicon M172 Can-Bus Master with TM172E28R slave

Hello, 

 

I am using a expansion module TM172E28R on a TM172PDG42R controller with Machine Expert - HVAC software. 

I have setup my controller and software exactly like in this video from Schneider: https://www.youtube.com/watch?v=pyJA31G2yQk&list=PLa7UGrWOTyjlgMo0lD4eVCV0zFQYxbLoa&index=7 

I have setup up the controller as Can-Bus Master address 125 and the TM172E as slave address 1, also the dip switches are set (4-5-6 all off), the dip switcdh number one is on and is the EOL resistor. 

I have also added a 120 Ohm resistor on the Can-Bus terminal from the M172P. 

Somehow i cannot get the Master running with the slave running. 

The sys variables for the CANbus communication is all zero. 

I also have a input from the expansion module in my watch and its always false (voltmeter shows me 24VDC). 

Is there anything what I can try else? Or is there a setting i need to set that is not in the manual? 

The Firmware of TM172P is "596.10".

 

Any help is appreciated. Thank you.

 

Regards, 

 

Michael

Tags (2)

Accepted Solutions
Bastian_Schmitz
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
1
337

Re: Modicon M172 Can-Bus Master with TM172E28R slave

Did you made a download all? Only in that case the CONNEC.PAR which is used for the communication will be downloaded. On the expansion is near the CAN Port a LED. Is this LED flashing? What is the status of sysCANopenNodeStauts[3]?

See Answer In Context

Tags (1)
2 Replies 2
Bastian_Schmitz
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
1
338

Re: Modicon M172 Can-Bus Master with TM172E28R slave

Did you made a download all? Only in that case the CONNEC.PAR which is used for the communication will be downloaded. On the expansion is near the CAN Port a LED. Is this LED flashing? What is the status of sysCANopenNodeStauts[3]?

Tags (1)
Mick0275
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
0
130

Re: Modicon M172 Can-Bus Master with TM172E28R slave

Thanks for your help, that LED was not flashing, it was a wire mistake on the bus. 

It works now.

Tags (1)