Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
You can subscribe to this forum after you log in or create your free account..
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
Posted: 2019-05-08 12:32 AM
01.03 no of ABB VSD is connected to the AS-P via Modbus-RTU as slave Devices.
02.These VSDs are going to control via BMS.
03.The Control Point Configuration has attached here.
Requirement
01.These VSDs must be operated as BMS command after a power failure
Issue
In first startup, the VSD does not operate according to the BMS Command. But after one more start & stop command, it started to operate properly via BMS. It occurs mainly after an power failure. But ABB VSD Vendor exhibited this function using ModBusPoll software. First he commanded to the VSD & shutdown Power of VSD. After powerup the VSD again, it was operated with the command. But this was not happend in Struxureware.
Please give me a solution as soon as possible.
As my observation, this VSD vendor, initially configured Modbus operating point(Register) as a reable & writable point. But it did not worked. Then he configured that point as only writable point & it operated properly
Posted: 2019-05-08 04:49 AM
Hello @Jean_Commeignes , I think you can help @ajith_iqsystems for the issue above
Posted: 2019-05-09 08:46 AM
Please give me a solution for this issue as soon as possible
Posted: 2019-05-15 07:15 AM
Hello Ajith,
Would be more than happy to help.
I seem understanding that your Modbus communication issues with ABB VSD, are in the scope of Building Management Systems, for HVAC control aplications (and not Industrial Automation Systems).
If I am right, could you please tell me what is or what are Schneider Electric BMS controller or server ranges involved?
Best regards
Jean
Power & Building Exchange Community Manager
Posted: 2019-05-15 07:22 AM
Sorry Ajith,
Lately saw your previous post, explaining your issue, I could understand.
So, will connect with you through private message, as this forum is Industrial Automation focused.
Jean
Power & Building Community Manager
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.