M580 - CompactLogix PLC explicit communication

Solved
desa
Crewman
Crewman
0 Likes
2
1259

M580 - CompactLogix PLC explicit communication

Hi,

 

Could anybody help me to setup explicit communication using the DATA_EXCH block without being a CIP expert?
I read the docs here: https://www.se.com/ng/en/faqs/FA409179/
The example of the CIP request in the last page of the pdf is the following:

 
 

The meaning of the registers - as I figured out - are:

00: 0252 - I don't know what the 0x02 means, the 0x52 is the service code of the unconnected send request.

01: 0620 - 0x06 is the class ID of the connection manager, but what is the byte 0x20?

02: 0124 - I suppose 0x01 is the connection manager instance number, what is the instance segment 0x24?

03: 1007 - timeout ticks & priority/tick time, does it depend on the partner or this value will be ok?

04: 000C - number of bytes from the next register to the "Data: 0001" row.

05: 044C - 0x04 is the number of words from the next register to the end of the tag name, 0x4C is the Rockwell read tag service.

06: 0591 - 0x05 is the number of characters in the tag name, 0x91 is a constant to read a tag by name.

07: 6170 - from here comes the name of the tag.

08:

09:

10: 0001 - number of elements to read.

11: 0001 - 0x00 reserved, 0x01 route path size. Does it mean we use one word from the next register (EIPRequest[12]).

12: 0001 - 0x00 route path address, is this the slot number? 0x01 is the port. Why is this 0x01? Is it always 0x01?

 

If I try this example with a 1769 Rockwell PLC and created the "parts" variable. A Wonderware CIP DA server can read it, but the response in the M580 PLC is:

00D2 - ????

0006 - by the docs this means "Only part of the expected data was transferred"

 

On the address pin of the DATA_EXCH block the value is: ADDMX('0.0.3{192.168.0.161}UNC.CIP').

 

I cannot guess the exact meaning of the following bytes:

00 MSB: 0x02 - request path size

01 LSB: 0x20 - segment, path segment

02 LSB: 0x24 - instance segment

03: 0x1007 - timeout ticks & priority/tick time

11: 0x0001 - route path size

12: 0x0001 - route path address, route path port

 

Any help would be appreciated

Tags (3)

Accepted Solutions
JerryBartlemay
Ensign Ensign
Ensign
0 Likes
1
1251

Re: M580 - CompactLogix PLC explicit communication

Hello, desa,

 

You're in luck.  Early this year I completed a white paper on this topic, with a pair of companion DFBs.  The document you reference was a key to figuring out a solution.

 

I've attached the document and DFBs.

 

Feel free to message me if you have questions.

See Answer In Context

Attachments
Tags (2)
2 Replies 2
JerryBartlemay
Ensign Ensign
Ensign
0 Likes
1
1252

Re: M580 - CompactLogix PLC explicit communication

Hello, desa,

 

You're in luck.  Early this year I completed a white paper on this topic, with a pair of companion DFBs.  The document you reference was a key to figuring out a solution.

 

I've attached the document and DFBs.

 

Feel free to message me if you have questions.

Attachments
Tags (2)
desa
Crewman
Crewman
0 Likes
0
1245

Re: M580 - CompactLogix PLC explicit communication

Hello Jerry,

 

Two hours ago we were able to successfully communicate with the Rockwell PLC. The only problem was we forgot to write the message length in the management parameters. It is working fine now. As I saw you created special FBDs to read/write variables.

We are going to try your blocks. 

Thank you!

 

Yours sincerely:

Dezső Sajtos