New in the Community? Get started here

Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
Industry Automation and Control Forum
This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.
cancel
Showing results for 
Show  only  | Search instead for 
Did you mean: 
Highlighted
Lieutenant JG

M340/M580 reading Input Registers / Coils / Contacts (1, 10001, 30001 etc) using DTM Browser configuration

Hi all,

 

We've recently tried to use the DTM Browser to communicate with a ModbusTCP device which has data available for reading on register 30001 upward, and data for writing to at 40001 and upward.  I would have expected this to be a common situation, where the DTM Browser Generic ModbusTCP Device would be suitable, however on investigation, the ModbusTCP DTM Browser Generic Device is only able to access 40001 Holding Registers.

 

Has anyone come across the same issue?

Was there a workaround found (which didn't involve the use of DATA_EXCH / READ_VAR)?

 

Regards,

Bevan

1 REPLY 1
Ensign

Re: M340/M580 reading Input Registers / Coils / Contacts (1, 10001, 30001 etc) using DTM Browser configuration

As far as I know IO-scanning (DTM browser) only allows for reading/writing 4XXXX (%MWxxx) registers, meaning only the Modbus function codes 3, 16 and 23 are supported.

Other Modbus function codes, reading/writing 0xxxx, 1xxxx and 3xxxx are supported by function blocks only.

RoozeeR