M251 Modbus server fc4

Highlighted
Cadet

M251 Modbus server fc4

Hi, 

can be set, to make the modbus server respond to function 4 (read input register ) ?

 

Thanks.

Tags (1)
2 REPLIES 2
Highlighted
Administrator

Re: M251 Modbus server fc4

@AmeliaFaraci : Could you help?

Rodrigo G. 


Industrial Automation Community manager

Tags (1)
Highlighted
Crewman

Re: M251 Modbus server fc4

Hi @Jeneburg ,

 

If you take a look in the page 104 of the "Modicon M251 - Logic Controller - Programming Guide" :

https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=EIO0000003089.02.pd...

 

If I am not wrong based on the document the FC4 is not supported for Modbus TCP Server but if the client uses FC3 you can move the %IW to %MW in the controller.

 

I hope this helps you.