Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • Industrial Automation
  • :
  • Industry Automation and Control Forum
  • :
  • Problem in reading bacnet objects from m172p
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49466members
Join Now
242757posts
Join Now

M172 and SER8300 integration over BACNET MS/TP

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to Industry Automation and Control Forum
jyoon
Crewman jyoon
Crewman
‎2020-06-04 05:15 AM
0 Likes
6
1470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-06-04 05:15 AM

M172 and SER8300 integration over BACNET MS/TP

We are trying to connect M172 and SER8300 over BACNET MS/TP using Machine Expert HVAC.  How can we read the anlaog values (Temp and Humidity, etc) using M172 from SER8300?  Currently, SER8300 is connected to M172 RS485-1 (BACNET MS/TP).  We already changed COM (MAC) value from 254 to 10.  Thank you very much for your help!

Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
6 Replies 6
CraigEl
Administrator CraigEl Administrator
Administrator
‎2020-06-04 08:46 PM
1 Like
4
1456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-06-04 08:46 PM

Re: M172 and SER8300 integration over BACNET MS/TP

I don't know much about the M172 but from what I can tell it's BACnet MS/TP capabilities are fairly limited. When we use it in Hotel situations we generally connect to the SE8000 using modbus. From SE8000 firmware version 1.3 and later modbus is inbuilt.

 

You can find the SE8300 Modbus Integration Guide on the Exchange.

 

You can find the selection of BACnet/Modbus in the SE8000 network menu

 

se8kModbus.png

Share
Reply
jyoon
Crewman jyoon
Crewman
‎2020-06-08 02:51 PM
0 Likes
3
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-06-08 02:51 PM

Re: M172 and SER8300 integration over BACNET MS/TP

Now we changed it to Modbus. RS485-2 +, - and ground are connected with COM address of 10.  I am having trouble opening up the document link.  Do you have any wiring diagram as well?  I believe I need to install a resistor/resistors at a terminal device but I wasn't sure.  Currently, we only have two devices.  We have M172 on one end and SER8300 on the other.    So do I need to install resistor on both ends?    

 

Thank you very much for your help!

Share
Reply
CraigEl
Administrator CraigEl Administrator
Administrator
‎2020-06-08 06:15 PM
0 Likes
2
1436
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-06-08 06:15 PM

Re: M172 and SER8300 integration over BACNET MS/TP

Don't connect the SE8000 ground terminal, I know it's not intuitive...

 

The following is an extract from a presentation for the Hotel Room Solution (HRC) that is based on the M172. You will want to have a 120 ohm resistor at each end, this is standard practice for RS485.

 

HRC_SE8K.png

Share
Reply
jyoon
Crewman jyoon
Crewman
‎2020-06-09 01:11 PM
0 Likes
1
1427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-06-09 01:11 PM

Re: M172 and SER8300 integration over BACNET MS/TP

Thank you.  I disconnected it now but had it connected before.  Do you think this may have made the equipment inoperarable?  I attached screetshots for configuration of Modbus Slave.  Do I need to have programming file as well?  I don't think I am establishing the serial connection at all.  Thank you.

 

Attachments
Share
Reply
GeorgeL
GeorgeL Cadet
Cadet
‎2020-07-06 12:19 PM
0 Likes
0
1257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:19 PM

Re: M172 and SER8300 integration over BACNET MS/TP

Hi there, 

 

Just came across your question. Has it been solved? 

 

If not, were you able to see the Device present in ESME HVAC software? 

 

You can do it by dragging Highlighted Target variable to your watch window.

 
 

 

 

 

Attachments
Tags (1)
  • Tags:
  • english
Share
Reply
Majid
Majid
Cadet
‎2020-09-13 03:37 AM
0 Likes
0
752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-13 03:37 AM

Problem in reading bacnet objects from m172p

hi , i have m172p 42 io 

I want to use it to connect modbus device variables to bacnet ip network

Please tell me how to read the present value of the bacnet variables to use it in the program

Tags (1)
  • Tags:
  • english
Share
Reply
Top Experts
User Count
andrea_romacco
Crewman andrea_romacco
1
Fleo
Crewman Fleo
1
sesa25402
Administrator sesa25402 Administrator
1
Bastian_Schmitz
Ensign Bastian_Schmitz Ensign
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric