Is it possible to use VSD as a power supply for the CNC machines?

dears;

 is it possible to use VSD as a power supply for the CNC machines ,

for example , i need  to use ATV650D55N4 as a regulated power supply for a CNC machine type ehrt holecut 40-10 cnc , is it accepted ? 

 

regards 

1 REPLY 1
Highlighted
Lieutenant JG

Re: Is it possible to use VSD as a power supply for the CNC machines?

Are you think to use a VSD for a single phase to three phase converter?

 

In general, I would not recommend this approach.  VSDs are quite complex devices, and generally expect certain things from their field systems (i.e. short circuits incredibly unlikely, thermal model equivalent to a large lump of steel, inductive loads).

 

If you are disconnecting loads suddenly (as would happen if a CNC machine is switching its own 240/415 power) the VSD will likely trip or produce unreliable voltages/frequencies.

 

A VSD is really a 'Variable Speed Drive', it's not intended for us as a power supply.