Industry Automation and Control Forum
This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-21 02:32 AM
I'm having issues linking variables from a m221 .SMBP project to a new Vijeo project.
The .SMBP project displays find when searching for the file but when i click "Open" there are no variables found.
I have tried different .SMBP projects i have but all have the same result.
Versions
Vijeo Designer 6.2.12
Machine Expert Basic 1.2 SP1
Any help will be greatly appreciated.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-23 06:14 AM . Last Modified: 2024-02-23 06:52 AM
Hi
I'm not an expert in MachineExpert-Basic. But have you checked that you have selected "IEC61131 Syntax" on the driver side in vijeo?
And make sure that you have generated the symbols in MachineExpert-Basic:
Here the full FAQ:
Greetings
|
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-29 12:48 AM
Thanks for your help. I had this done yes, turned out I had the project password protected and this was stopping the Vijeo software from reading the variables.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.