Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
80977members
347153posts

How to connect HMIST6400 to TM221CE24R PLC?

Solved
jhonut
Ensign
Ensign
0 Likes
3
1774

How to connect HMIST6400 to TM221CE24R PLC?

Hello,

I'd like to connect a HMIST6400 (programmed with ESOTE) with a TM221CE24R PLC (programmed with MachineExpert Basic).

I have exported the PLC symbols, but MEB allows only the .csv format which is not recognized by HMI.

How could I connect these two devices?

Tags (1)

Accepted Solutions
Bastian_Schmitz
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
1
1759

Re: How to connect HMIST6400 to TM221CE24R PLC?

The way is easier than you expect.

Add a SE Modbus TCP driver (or SIO)

And then import the Basic file via symbol import

 

See Answer In Context

Attachments
Tags (1)
3 Replies 3
Bastian_Schmitz
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
1
1760

Re: How to connect HMIST6400 to TM221CE24R PLC?

The way is easier than you expect.

Add a SE Modbus TCP driver (or SIO)

And then import the Basic file via symbol import

 
Attachments
Tags (1)
LeTomas
Lieutenant Lieutenant
Lieutenant
0
1746

Re: How to connect HMIST6400 to TM221CE24R PLC?

Dear @jhonut ,

 

I have made the next video of how to connect the HMISTO7 to a M221.... is the same for the HMIST6****:

 

https://schneider-electric.box.com/s/av7nek0zbdltp6oh7qfuysfiimx2uomh

 

Best regards,

 

Letomas

Tags (1)
jhonut
Ensign
Ensign
0 Likes
0
1744

Re: How to connect HMIST6400 to TM221CE24R PLC?

Thanks for your reply, @Bastian_Schmitz !

I have done as you suggested but I get an error: "Invalid device address. Enable or disable IEC address mode in the equipment." How should I do this? It's true that I don't use Modbus addresses but memory addresses.

Later edit. I have seen the video suggested by @LeTomas and I've how he's done it.

Tags (1)