HOW TO INSALL A BY PASS COTACTOR IN ATS 22 ?

WAWERU
Cadet

HOW TO INSALL A BY PASS COTACTOR IN ATS 22 ?

Can soft starter  ATS22 control external by pass 

Tags (1)
3 Replies 3
gsterling
Commander Commander
Commander
0 Likes
1
851

Re: HOW TO INSALL A BY PASS COTACTOR IN ATS 22 ?

Hello Waweru

 

For which related Schneider software product are you logging this question?

 

This post may be to the wrong team, so we'd like to make sure your question is directed at the proper group.

 

Regards

 

Greg Sterling

Tags (1)
Kassandra
Crewman
Crewman
0 Likes
0
764

Re: HOW TO INSALL A BY PASS COTACTOR IN ATS 22 ?

Thanks for the information, keep sharing this type of info Upsers

Tags (2)
BJacqz
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
549

Re: HOW TO INSALL A BY PASS COTACTOR IN ATS 22 ?

Hello,

The Altivar ATS22 has already internal by pass contacts so there is no need to add external one.

ATS48 can have external by pass as option. In addition this Soft Starter continue to monitor the motor current and also continue to perform motor protection.