EcoStruxure operator terminal expert animation problem

Solved
baterija
Crewman
Crewman

EcoStruxure operator terminal expert animation problem

Hello

 

I am using ecoStruxure operator terminal expert. 

Is it posible to make an animation of object in correlation of variable value. 

 

For example. 

I am having a switch object and i am using it for input for var1 to control motor. Now i want to animate switch color by the value in Var2. Is this posible? I need this for indication if motor is runing in auto or manual mode and if it is standing or error, so at least 4 diferent status. And also i want to change texts for the sam status. 

 

Thanks

Tags (1)

Accepted Solutions
Lukas
Crewman Crewman
Crewman

Re: EcoStruxure operator terminal expert animation problem

2 Replies 2
Lukas
Crewman Crewman
Crewman

Re: EcoStruxure operator terminal expert animation problem

TomDroll
Lt. Commander Lt. Commander
Lt. Commander

Re: EcoStruxure operator terminal expert animation problem

 

 

Hi, you can BIND a  variable for the ON and OFF state, of the switch - Properties dialog ->Shape->Basic then Off or On state Fill (or Border) color pallet. 

 

See attached screen shot.

Tom Droll