I want to create a DFB that can be used on either a M580 or M340 using a READ_VAR.  The M580 uses the ADDMX, while the M340 uses the ADDM.  Is there a way for the DFB to determine its processor so that it can call the correct function?

Tags (1)

Accepted Solutions
Michael_Chan
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
1043

Re: Determine M580/M340 from with its program

I'm thinking of a simple solution for you.

In your creation of DFB, create a BOOLEAN input pin to determine M580 or M340, e.g. Logical 0 = M580; Logical 1 = M340.

When a PLC programmer instantiate a DFB, he/she just need to setup a value to this input pin, logical 0 or 1.

Hopefully this solution is fine for you.

Michael Chan Kum Yuen

See Answer In Context

Tags (1)
JerryBartlemay
Ensign Ensign
Ensign
0 Likes
0
1026

Re: Determine M580/M340 from with its program

Actually, there is no need.  The ADDM works in both the M340 and M580; that's why it shows up in both libraries.  ADDMX is used for addressing at a serial link module port.  Check Control Expert Help.  It will show you the use cases.

See Answer In Context

Tags (1)
3 Replies 3
Michael_Chan
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
1044

Re: Determine M580/M340 from with its program

I'm thinking of a simple solution for you.

In your creation of DFB, create a BOOLEAN input pin to determine M580 or M340, e.g. Logical 0 = M580; Logical 1 = M340.

When a PLC programmer instantiate a DFB, he/she just need to setup a value to this input pin, logical 0 or 1.

Hopefully this solution is fine for you.

Michael Chan Kum Yuen
Tags (1)
Richard
Lieutenant Lieutenant
Lieutenant
0 Likes
0
1033

Re: Determine M580/M340 from with its program

There are some status words that can also help with this.

 

%SW14 contains the commercial version of the processor.

%SW16 contains the internal firmware version number which is likely to be different between M340 and M580.

%SW146 and %SW147 contain the serial number of the SD card. The M340 requires a serial card but the M580 does not and will return zeros if there is not a card present. Obviously this method fails if your M580 has an SD card installed for logging data or other purpose.

 

These should give you what you want and a few other indicators for management of the program.

Tags (1)
JerryBartlemay
Ensign Ensign
Ensign
0 Likes
0
1027

Re: Determine M580/M340 from with its program

Actually, there is no need.  The ADDM works in both the M340 and M580; that's why it shows up in both libraries.  ADDMX is used for addressing at a serial link module port.  Check Control Expert Help.  It will show you the use cases.

Tags (1)