Communication between M172 and TM172DCL

Highlighted
Crewman

Communication between M172 and TM172DCL

Hi,

 

I am trying to connect TM172DCL (Display for M172) but I keep getting Modbus Comm error.

 

Current Setting:

1.  I am using RS485-2 as a Modbus Master on M172.

2.  Created a Generic Modbus Device for TM172DCL.

3.  Since they both have the same power source, I left ground disconnected.

4.  Installed 120 ohm to TM172DCL.  Maybe I need to install 120 ohm on M172 as well?

 

Can you tell me what I am doing wrong?  I need to be able to exchange variables between them but It seems that RS485-2 link on M172 is dead.

 

Thank you for your help!

 

Jung

Tags (1)
2 REPLIES 2
Highlighted
Crewman

Re: Communication between M172 and TM172DCL

Hi @jyoon ,

 

When I work with the M172D I usually use it as a master in the communication because for me is much simpler to exchange the information between the devices.

Take a look on this presentation of how to connect both devices (M172 plc as slave): 

https://schneider-electric.box.com/s/ld78b6pxs08l0tb7qgz3eix01hha5wpt

Project: https://schneider-electric.box.com/s/kcwhv7kxtat0shm20njyzzc87azx4dkk

 

In your case if something is not working you should try to check:

 

1) The connection from the M172 RS-485 2 to the display (you can check the connection in my presentation but with RS 485-1).

2) The Actual values on the modbus configuration on the M172D and the PLC (They must match).

3) Verify the registers that you want to read from the M172D.

 

I hope this helps you 👍

 

Tags (2)
Highlighted
Crewman

Re: Communication between M172 and TM172DCL

Hi, @LeTomas 

 

Thank you very much for your help.  I followed it and everything is working fine now.

 

Jung