A forum addressing machine automation solutions for the complete machine lifecycle. Including offers like Machine Advisor, Modicon PLC/PacDrive, Lexium or Preventa. Discuss and share knowledge on offers relating to cloud-based service platforms, machine localization and monitoring, industrial operations control, motion products as well as safety function!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-06-15 05:06 PM . Last Modified: 2020-09-10 12:26 AM
I'm working on M172 controllers and need to use BACnet protocol.
Anybody know where can i download BACnet Addons Library for Ecostruxure Machine Expert HVAC?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-06-16 11:18 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-06-24 12:30 AM
Hi Anawat,
As discussed, the best in this case is to use a workaround, as by using a mirror point and alarm object in EBO system.
Pier
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-06-16 11:18 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-06-20 05:49 PM
Hi Pier,
I am able to discover MP172 BACnet device and objects into EBO.
i have one issue about alarm and reset text Message of BI object. These are not propertied in ESME to add.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-06-22 06:11 AM
Hi,
the string fields can be edited only from the PLC (they are read-only)
You can double check on the PICS which properties are implemented (https://www.bacnetinternational.net/btl/index.php?m=266) - they are in line with the AAC profile.
Please contact me directly to investigate further and then we can report here the findings.
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-06-24 12:30 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-06-24 12:30 AM
Hi Anawat,
As discussed, the best in this case is to use a workaround, as by using a mirror point and alarm object in EBO system.
Pier
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-28 09:38 AM
Hello,
we are using Bacnet Library 2.3 version within M172 controllers for AHU application and we experience random disconnections from the network. We've moved Bacnet task from background to timed task (we believe their priority is higher), also made longer timeouts on Bacnet line in AS-P, situation got a lot better, but not perfect - disconnections still occurs. Do you have any ideas ?
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-02 02:23 AM
I'm not found this error before. You can try to check the below link. It might be help.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-25 01:11 AM
Hello Pierpaolo,
I 've the same kindly request but concerning Modbus. Would you like to send al link to MODBUS Addons Library for Ecostruxure Machine Expert HVAC?
Thanking in advance,
Artur
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-26 01:53 PM
Hi,
By default the Modbus Addon "ModBUS_Addons_M172P_O.plclib" is under the folder :
"C:\Program Files (x86)\Schneider Electric\EcoStruxureMachineExpertHVAC\Catalog\FreeAdvance\PLC"
BR
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.