Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • Industrial Automation
  • :
  • Industry Automation and Control Forum
  • :
  • A standard relay can't be used in a Safety Instrumented Function (SIF)
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49224members
Join Now
242436posts
Join Now

A standard relay can't be used in a Safety Instrumented Function (SIF)

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to Industry Automation and Control Forum
GMInternational
Lieutenant JG GMInternational
Lieutenant JG
‎2020-03-12 06:11 AM
1 Like
2
513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-12 06:11 AM

A standard relay can't be used in a Safety Instrumented Function (SIF)

safety_relay.jpg

Safety Relays are devices that implement safety functions. In the event of a hazard, a safety relay will work to reduce the risk within an acceptable level. When an error occurs, the safety relay will initiate a safe and reliable response. Each safety relay monitors a specific function. By connecting it to other safety relays, it is possible to achieve a total monitoring of a machine or plant. Safety relays are a simple and efficient way to meet existing safety standards, resulting in safe operations for the personnel and the equipment as well as a long service life. Risk reduction should be a priority for any business, in order to protect the employees and reduce the risk of costly accidents or equipment replacement. Generally, if a risk can be reduced, then it should be.

Some of the functions that safety relays include:

 

  • Stopping a movement in a controlled and safe manner
  • Monitoring the position of movable guards
  • Interrupting a closing movement during access
  • Emergency off/stop

Safety relays are simple to operate and have a clear structure. The use of safety relays has become widespread due to their compact design, high reliability, and most importantly they meet all the required standards. They have become an integral component of any new plant or machine where safety functions are necessary. A standard relay can’t be used in a Safety Instrumented Function (SIF). For this reason, whenever it is necessary to use a relay complying with IEC 61508 and the relevant industry standard (for example 61511), we must refer to a safety relay.

SIF refers to equipment designed to prevent or mitigate the risks of a specific hazard. It detects the imminence of an incident, decides to take a specific action and acts to bring the process back to a safe state.

A SIL (Safety Integrity Level) certified relay (Safety Relay) has a known and guaranteed ability to perform a given Safety Function and reach a specific safe state on demand (i.e. open a relief valve or activate a Fire Extinguishing System). The typical cases of application of a SIL certified relays are represented by a controller that can’t meet the power requirement (V or A), or when the multiplication of the contacts is required, or the controller safety function must be inverted.

SIL (Safety Integrity Level) Certified Relays are used for critical loops where careful consideration should be given to Line and Load Monitoring. In applications, such as F&G systems, line and load monitoring are fundamental, and Smart Relays become a valuable tool. Smart Relays are devices that implement the load and line diagnostics functions to the safety functions of a safety relay.

The SIL certified relays are not used exclusively in Oil & Gas or Petrochemical industries, they are also a must in many other industries like railways, cars and lift, power distribution and anytime a failure of the relay can cause a serious accident.

GM International designs, engineers and manufactures a complete range of Intrinsically Safe and SIL Certified relays. Thanks to specific contact arrangement, GM International relay modules maintain higher level of safety while improving process availability (a single fault is not enough for a spurious trip of the load).

In conclusion, you should never consider safety and availability mutually exclusive. Choosing the right SIS can ensure that your personnel and your plant are perfectly safe without you having to suffer any economic loss.

Labels
  • Smart Design & Engineering
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
2 Replies 2
Omaelk
Administrator Omaelk Administrator
Administrator
‎2020-03-17 12:46 PM
0 Likes
0
491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-17 12:46 PM

Re: A standard relay can't be used in a Safety Instrumented Function (SIF)

@KalyanMeduri  if you want to read this one 😉

 

Share
Reply
BevanWeiss
Admiral BevanWeiss
Admiral
‎2020-03-23 03:23 AM
1 Like
0
460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-03-23 03:23 AM

Re: A standard relay can't be used in a Safety Instrumented Function (SIF)

Can you provide a reference for the statement:


A standard relay can’t be used in a Safety Instrumented Function (SIF).

Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Share
Reply
Top Experts
User Count
andrea_romacco
Crewman andrea_romacco
1
Fleo
Crewman Fleo
1
sesa25402
Administrator sesa25402 Administrator
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric