Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
2 wire and 4 wire transmitters on the same STBACI1400 module?
Industry Automation and Control Forum
This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-12-1105:34 PM
2 wire and 4 wire transmitters on the same STBACI1400 module?
Hi,
a customer brought up this rather simple question but i would like to confirm if there would be any interference in signal if we wire let's say a 2 wire transmitter on channel 1 and a 4 wire transmitter on channel 2. They would have to share the same return on pin 3.
Below are the schematics for 2 wire and another for 4 wire. But we do not have documented anywhere a mix of both. Appreciate the help! Thanks
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-12-1210:54 AM
Hi Gilly, the answer has to be "it depends". The four wire transmitter is externally powered. If its power source is electrically isolated from the signal, then it should be okay. If, however, the transmitter shares commons between power and signal, or if they are referenced to ground, that spells trouble. To be safe, I would use a signal isolator in the four wire transmitter circuit to ensure isolation.