APC, part of Schneider, lines of products: PDU, UPS, environmental monitors communicate over SNMP.
I have costumers who want to be able to control them through the Automation Server, example the AS reads from the UPS that the UPS battery is low or that the temperature in a room is to high and starts turning off outputs on a power outlet and then over modbus it may also open G3 circuit breakers.
The idea would be add an SNMP interface just like there is a Modbus and BACnet one already. Using as a reference the Modbus Interface, you would add a client then set in its properties the host and auth settings, Then under the device have the options to add points of the different types and instead of putting a register address inputting the OID.
The main goal is better integration of Schneider different lines of products and for the AS to tap into the wide range of SNMP devices.