APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:09 AM . Last Modified: 4 weeks ago
I bought a BX1300LCD. I am connected to a computer, LCD monitor, external HD, modem, router, speakers, and a laser printer for UPS. I have the following questions:
1 - I want to know if I bought was right, maybe I can be more energy-efficient one. Mountain laser printer, connected to the backup to attract a lot of power (wattage indicator to a 800W) and equipment began beeping, so I connected the printer surge only.
3 - It was on this device in his review to complain about a noisy fan. It has a fan? I did not hear.
PS I finally did not in April surge protection (other companies) began to beep every time I print, even if the printer is connected to the surge only plug-ins. I called to them, they say it is because I do not have AVR's. I think this is nonsense. Do you guys think?SORRY for my poor english and grammar
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:09 AM . Last Modified: 4 weeks ago
What you bought sounds correct for the rest of your load, but a laser printer should generally be plugged into an entirely separate outlet or surge protector, not into the UPS at all. The reason for this is that it can cause a voltage sag on the internal circuits of the UPS, similar to the effect that you would observe if you turned on a hair dryer in a bathroom or if your air conditioner kicks in. In these situations many people observe a momentary, or permanent dimming of lights in the room until the dryer/AC is turned off. I have not heard of any issues with the fan on the BX1300LCD being "too loud"...it may be slightly audible when it is charging the battery but to my knowledge we have had no issues with it being abnormally loud.
You are correct, AVR has nothing to do with the beeping or laser printer issue. AVR strictly relates to what the unit measures for input voltage coming from the outlet/mains.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 02:09 AM . Last Modified: 4 weeks ago
What you bought sounds correct for the rest of your load, but a laser printer should generally be plugged into an entirely separate outlet or surge protector, not into the UPS at all. The reason for this is that it can cause a voltage sag on the internal circuits of the UPS, similar to the effect that you would observe if you turned on a hair dryer in a bathroom or if your air conditioner kicks in. In these situations many people observe a momentary, or permanent dimming of lights in the room until the dryer/AC is turned off. I have not heard of any issues with the fan on the BX1300LCD being "too loud"...it may be slightly audible when it is charging the battery but to my knowledge we have had no issues with it being abnormally loud.
You are correct, AVR has nothing to do with the beeping or laser printer issue. AVR strictly relates to what the unit measures for input voltage coming from the outlet/mains.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.