I need to know if i can hook this unit from the data port to the network verses the data port to usb. of pc.
Thank you mark
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:55 AM . Last Modified: 2024-03-22 02:58 AM
Ty very much
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:55 AM . Last Modified: 2024-03-22 02:58 AM
Hi Mark,
That would not work because it is not a true network port. The RJ-45 to USB cable that comes with the UPS is the only way to communicate with it. If you would like to have a network enabled UPS I would suggest a Smart-UPS with a Network Management Card (NMC). Most likely the SUA1500 and a AP9630.
Smart-UPS: http://www.apc.com/products/family/index.cfm?id=165
NMC: http://www.apc.com/products/family/index.cfm?id=98
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 01:55 AM . Last Modified: 2024-03-22 02:58 AM
Ty very much
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.