I have a back-ups es 750 that just started making a constant beep with a red light that looks like 2 batteries. I turned it off and on and it gave a long beep and then started constantly beeping again. Does the battery need to be replaced? How do I order one and what is the cost?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:57 PM . Last Modified: 2024-03-19 11:44 PM
Hi,
Is the unit beeping every second or is there a constant tone? If the unit is beeping every second that indicates low battery but the beeping should stop when AC is available and the battery should charge. If there is a constant tone that indicates the battery in disconnected, needs to be charged, or is at the end o f useable life. Section 3 of the user’s guide lists the status indicators i.e. what each alarm means.
User's Guide http://www.apcmedia.com/salestools/KBOK-766PMZ/KBOK-766PMZ_R2_EN.pdf?sdirect=true
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-11 10:57 PM . Last Modified: 2024-03-19 11:44 PM
Hi,
Is the unit beeping every second or is there a constant tone? If the unit is beeping every second that indicates low battery but the beeping should stop when AC is available and the battery should charge. If there is a constant tone that indicates the battery in disconnected, needs to be charged, or is at the end o f useable life. Section 3 of the user’s guide lists the status indicators i.e. what each alarm means.
User's Guide http://www.apcmedia.com/salestools/KBOK-766PMZ/KBOK-766PMZ_R2_EN.pdf?sdirect=true