APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:35 AM . Last Modified: Friday
I have a Smart UPS-750, Model # SUA750
I thought the unit was defective so I started a chat with APC support. One thing the tech said stuck in my mind but i only thought about the question afterwards.
He said something about the wattage and the maxium being 500W that should be plugged into the unit. Here are my questions:
1. Does this mean the unit should only be suppling 500W to everything that is plugged into the unit?
or
2. Does each outlet on the back of the unit have a max load of 500W?
3. What are the harms or what would happen if you had the UPS supply a lot more than 500W? Battery die faster? Will it break the UPS?
4. Does the UPS let you know if this is happening?
Thanks in advance for any info.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:36 AM . Last Modified: Friday
Hello:
On this unit, the maximum output is 500 watts (or 750 voltamps). This is for the entire unit. All outlets share a common bus and it does not make a difference which outlet you use.
You can monitor the load of the UPS either using our Powerchute software, a Network Management Card, or via the LED bargraph on the left side.
If you go over the maximum load (500w) the UPS will cease to output power, it will emit a constant tone, and the "Overload" LED will come on.
Let us know if there are more questions.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:36 AM . Last Modified: Friday
Hello:
On this unit, the maximum output is 500 watts (or 750 voltamps). This is for the entire unit. All outlets share a common bus and it does not make a difference which outlet you use.
You can monitor the load of the UPS either using our Powerchute software, a Network Management Card, or via the LED bargraph on the left side.
If you go over the maximum load (500w) the UPS will cease to output power, it will emit a constant tone, and the "Overload" LED will come on.
Let us know if there are more questions.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.