Hello,
We have bought an SUA3000RMI2U. The UPS is in a network configuration with 2 other PC's. Via a switch and 3G router the UPS has internet access.
The network provider has told us that the following smtp server should be used: mail.kpnmail.nl. No useraccount or password is needed and port 25 is used for sending e-mail. As far as I can tell, everything should work, but it doesn't. We get the following error messsage 'Test e-mail failed; smtp configuration error'. The primary DNS is set as the gateway address of the router: 192.168.1.1.
Any help to solve this issue is much appreciated.
Regards,
Rob.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 10:20 PM . Last Modified: 2024-03-20 03:04 AM
Hello,
We sorted out the problem. It appeared that the e-mail server had to be set to external (recipient) and not to local.
Regards,
Rob.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 10:20 PM . Last Modified: 2024-03-20 03:04 AM
Hello,
We sorted out the problem. It appeared that the e-mail server had to be set to external (recipient) and not to local.
Regards,
Rob.