Hi,
I have a APC Smart-UPS 700VA and basically I'm trying to use its DB-9 RS-232 interface port to connect it to a PC so I'm trying to see if I can connect it using a DB-9 to USB cable. Heres the thing, as soon as I connect the cable to the UPS, it powers down.
What am I doing wrong? Don't know much about UPS as its my first time using one.
Message was edited by: James Bond
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:10 PM . Last Modified: 4 weeks ago
Mr. Bond,
I believe the problem is that the DB-9 serial cable that is being used is not the standard APC Smart Signaling cable. The part number on that cable is 940-0024 and is approximately 3 feet in length, and black. Any standard straight-through serial cable connected to the serial port on the UPS will cause it to immediately power off.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:10 PM . Last Modified: 4 weeks ago
Mr. Bond,
I believe the problem is that the DB-9 serial cable that is being used is not the standard APC Smart Signaling cable. The part number on that cable is 940-0024 and is approximately 3 feet in length, and black. Any standard straight-through serial cable connected to the serial port on the UPS will cause it to immediately power off.