I was replacing the batteries to a Smart-UPS SC 1500 and I got the leads mixed up. Does anyone have a schematic for this power supply? I just need the wiring document for the 4 batteries.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:09 AM . Last Modified: 1 month ago
Apc Wont Offer Them But I Can Probably Get Them What Is The EXTACT Model Number Of The Ups
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:08 AM . Last Modified: 1 month ago
Smart-UPs SC 1500
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:08 AM . Last Modified: 1 month ago
I also have a Smart UPS 1000. Model SUA1000 AS0520323347
Any chance you could find a schematic for this?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:09 AM . Last Modified: 1 month ago
The four batteries in this ups (which I think has an RBC59 cartridge) are connected as two series strings which are in parallel with each other.... IE
( + ) ----- [+ Bat 1 -]---[+ Bat 2 -]---- ( - )
\ /
\--- [+ Bat 3 - ]---[+ Bat 4 -]--/
Hope my ASCII art doesn't get mangled in translation !
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:09 AM . Last Modified: 1 month ago
That Is Not The Exact model number what is the serial number
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:09 AM . Last Modified: 1 month ago
Apc Wont Offer Them But I Can Probably Get Them What Is The EXTACT Model Number Of The Ups
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.