I'm in the market for a rack mount UPS for an domestic office setting. Noise level of the UPS is a critical factor in the purchase, and unfortunately the APC website is grossly inadequate (if not misleading) in explaining the actual running noise levels for normal usage; even the Back-Up range is listed at 45 dBA giving little comprehension that in normal usage they make little (if any) noise until on battery.
I need the fan to not be running at all in normal usage if possible; of course, self-tests and running on battery are acceptable conditions where I would expect the fans to be on! The UPS is only there to support graceful shutdown of two NAS servers and a RS500 was doing the job before more than adequately - but it's given up the ghost now. For space reasons a rack mount option would now be best for me.
Are there any APC UPS that fill my criteria (and can be purchased in the UK) or should I shop elsewhere for another brand?
Message was edited by: quantock
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:01 PM . Last Modified: 1 month ago
SMX750, SMX1000, and SMX1500RM2U are 2U rack mount units that turn off the fan under normal conditions (input voltage is normal, not executing self-test or runtime calibration, battery temperature is normal).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:01 PM . Last Modified: 1 month ago
Not sure if there's a UPS that fits your need (maybe someone else here knows) but APC has [soundproofed racks|http://www.apc.com/products/family/index.cfm?id=468] for such environments. Specifications are here.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:01 PM . Last Modified: 1 month ago
SMX750, SMX1000, and SMX1500RM2U are 2U rack mount units that turn off the fan under normal conditions (input voltage is normal, not executing self-test or runtime calibration, battery temperature is normal).