APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:32 PM . Last Modified: 1 month ago
Just bought a new UPS RS 1000G yesterday, and I noticed that the battery was discharging. Today, it finally reached 0% and stated I needed to inspect the unit for a fault and the started beeping. I can't see any issues with it, other than the battery is discharging faster than the wall can charge it.
As far as I have observed, the unit has not gone on battery power once, always remaining on AC power.
Attached *.jpg is of the current status screen within powerchute.
Thoughts?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:33 PM . Last Modified: 1 month ago
Hi James,Can you use the display button right above the LCD screen of the UPS to go to the Event Counter just to make sure that the UPS didn't make any switches to On battery operation.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:32 PM . Last Modified: 1 month ago
Just bought a new UPS RS 1000G yesterday, and I noticed that the battery was discharging. Today, it finally reached 0% and stated I needed to inspect the unit for a fault and the started beeping. I can't see any issues with it, other than the battery is discharging faster than the wall can charge it.
As far as I have observed, the unit has not gone on battery power once, always remaining on AC power.
Attached *.jpg is of the current status screen within powerchute.
Thoughts?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:32 PM . Last Modified: 1 month ago
Just ran a self test on the unit via powerchute, and the battery charge went to 25%.
I waited another few minutes, it stated that it was at 23%, and I ran another self test, and it jumped to 34%.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:33 PM . Last Modified: 1 month ago
Hi Josh,
I would also advise for you to check if the battery is seated properly and also perform a brain dead on it. I have listed the procedure below on how to brain dead the BackUPS.
1: Disconnect any attached load.
2: Unplug the UPS from the wall socket
3: Disconnect the UPS' internal battery.
4: Push and hold the ""On"" button on the UPS for 5 seconds
5: Reconnect internal battery.
6: Plug UPS in to known good power source.
7: Turn UPS on.
Keep us updated on what will happen on your unit.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:33 PM . Last Modified: 1 month ago
I'm having exactly the same problem.
Bought the unit yesterday, installed it last night. All was well until I noticed this morning that the battery charge had gone to zero. No loss of power overnight.
Ran the self test and it passed. Charged the battery, briefly, to about 20%. Minute by minute the charge drops - now 8%.
Performed a 'brain dead' as descr1ribed. Same result.
Message was edited by: JamesRDavis
Wall power is clean and averages 118V. No intervening surge protectors, etc.
Message was edited by: JamesRDavis
Minimal demand on unit (about 200 watts).
Message was edited by: JamesRDavis
Something changed. For four hours it remained at 0% though the software said it was charging. Then it began to charge, very slowly. Two hours later it was at 48% charged. Two hours after that (now) it is at 54%.
I did nothing and the load remained constant.
Message was edited by: JamesRDavis
Next morning finds the XS 1000 battery fully (100%) charged.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:33 PM . Last Modified: 1 month ago
Hi James,Can you use the display button right above the LCD screen of the UPS to go to the Event Counter just to make sure that the UPS didn't make any switches to On battery operation.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.