I bought the RS 1000. When it arrived, it had to be charged before using the backup outlets. I plugged the computer into the surge protector outlet on the back and then due to the demands of tax season, only just now realized I had never gone back and plugged it into one of the battery backup outlets. I have tried that today and none of the battery backup outlets work...only the surge protector ones. Any help? I have since lost the booklet that came with it so have no instructions to help me out.
Thank you for any help you can give!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:46 PM . Last Modified: 3 weeks ago
The first thing I would check is the internal battery connections. Out of the box, the batteries inside the UPS are not connected. I think it is 2 grey connectors that you need to mate together to connect the battery.
Instructions for connecting the battery are in the product manual:
http://www.apcmedia.com/salestools/ASTE-6Z7V2K_R0_EN.pdf
Message was edited by: dirtfoot - fixed link
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:46 PM . Last Modified: 3 weeks ago
The first thing I would check is the internal battery connections. Out of the box, the batteries inside the UPS are not connected. I think it is 2 grey connectors that you need to mate together to connect the battery.
Instructions for connecting the battery are in the product manual:
http://www.apcmedia.com/salestools/ASTE-6Z7V2K_R0_EN.pdf